How to read individual bits from holding registers of VFDs in OCMC Configuration ? , I've tried typing the address like that 403201:0 or 403201.1 but it doesn't work .
I have restored the missing items. Please let me know if you have any issue.
Thanks! i just re-added the images and its all back :)
Thank you a lot ,
The problem was in the configuration of reading bits (as it was kept at default as you mention : Swap Bits were checked and the order is B1 B2 .. B16 ) So I need to swap when type the item reference .
For example
If I need to read bit 0 from the holding registers of VFD I need to type the address in this way ( XXXX : 16)
If I need to read bit 2 , I need to type the address in this way ( XXXX : 14)
If I need to read bit 15 , I need to type the address in this way ( XXXX : 1)
OR I can change the configuration by unchecking swap .
I'll go ahead in the first way I mention so not to rebuild the animation I've done .
Thank you again .
Great! I'm glad you got it sorted out!
Thanks for providing the feedback and present the final solution that worked for you.
Have a great day!