Power Operation OPC UA Tag Reading Issue Based On Number of Tags

Hello,

We used Power Operation v21 v8.30 in a project and we want to share some data through OPC UA Protocol. After I configured Power Operation as a OPC UA server, A third party OPC Client software (UaExpert) could connect but couldn’t open browse provider and can not read data. The project has got about 10,000 tags.

When I used another project which has about 1,200 tags, no issue and same third party OPC Client software (UaExpert) could connect and open browse provider and read data.

I tried adding tags manually for these two projects. For first big size project including 10,000 tags, third party OPC Client software (UaExpert) could not read data. However, for second small size project including 1,200 tags, third party OPC Client software (UaExpert) could read data.

When I check Power Operation System Guide with doc. no, date: 7EN02-0462-00, 07/2021. There is info about the tag number as “The OPC UA Server can support up to 100,000 tag subscriptions with 50,000 tag changes a second to the OPC UA client.”.

Ap-1: For large scale project (10,000 tags); the error message from third party software interface is attached as an image.

Ap-2: For small scale project (1,200 tags); Data reading from third party software interface is attached as an image.

Could anyone help me on this subject.

Parents
  • Hi  

    Could you check your installation folder, \Connectivity sub-folder for the file OPCUAServerConfiguration.config

    In this file, there are a few settings you may like to tune to enable larger tag counts in your system, the ones below are default settings:

    <MaxNodesPerBrowse>1000</MaxNodesPerBrowse>
    <MaxNodesPerRead>10000</MaxNodesPerRead>

    If you still experience issues when tuning these parameters (requires restart of Connectivity Service after making changes) it might be worth getting in touch with AVEVA Technical Support to troubleshoot this further.

    Kind regards

    Olivier

Reply
  • Hi  

    Could you check your installation folder, \Connectivity sub-folder for the file OPCUAServerConfiguration.config

    In this file, there are a few settings you may like to tune to enable larger tag counts in your system, the ones below are default settings:

    <MaxNodesPerBrowse>1000</MaxNodesPerBrowse>
    <MaxNodesPerRead>10000</MaxNodesPerRead>

    If you still experience issues when tuning these parameters (requires restart of Connectivity Service after making changes) it might be worth getting in touch with AVEVA Technical Support to troubleshoot this further.

    Kind regards

    Olivier