Reading custom fields using alarm properties does not work.

Hello. I'm KANG.

I'm using the alarm property to show the ability to read or write a value. Most are using analog alarms.

For example, if the name of analog alarm tag is 'AT0001', the setting value of High High can be read or written as 'AT0001.HighHigh'.

I registered a custom field among them.
However, if I try to read the value as 'AT0001.custom1', an empty string is returned.

What if I want to return the value entered in the custom field?

Version : Citect SCADA 2016 (Update Aug 13, 2019)

Parents
  • Hi ,
    This looks like a bug to me. It should return the custom value defined in the alarm tag configuration.
    As a work around, you could use the alarm browse function, then the get field functions, but it might not meet your needs.
    I'd recommend you reach out to Citect Support and get a bug raised for this issue to get it fixed.
Reply
  • Hi ,
    This looks like a bug to me. It should return the custom value defined in the alarm tag configuration.
    As a work around, you could use the alarm browse function, then the get field functions, but it might not meet your needs.
    I'd recommend you reach out to Citect Support and get a bug raised for this issue to get it fixed.