Created pump1.bearingtemp point does not has value update.

I followed the "Creating Points for Interfaces" to create a point named "pump1.bearingtemp". Check the value and it stays in "configure". No value update.

In the interface PI Message Log in PIINT01, it logged the following:

I 16-May-24 21:06:22 opcint_ReadOnly:OPCpi:OPC | 1 | 0                               (4)

 >> Time between here & OPC is : 0

    Time between PI & here is : 0

    Time offset applied to interface generated timestamps :0

    Time offset applied to OPC Server generated timestamps: 0

I 16-May-24 21:06:22 opcint_ReadOnly:OPCpi:OPC | 1 | 0                               (4)

 >> Poll Group 4 named 'Poll3'.

I 16-May-24 21:06:22 opcint_ReadOnly:OPCpi:OPC | 1 | 0                               (4)

 >> AddItems failed for tag pump1.bearingtemp, type VT_R4: The ItemID is not in the server address space (c0040007)

W 16-May-24 21:06:22 opcint_ReadOnly:OPCpi:OPC | 1 | 0                               (3)

 >> OPC server only accepted 0 out of 1 points, which is less than the configured (/rp) minimum threshold of 80%.

It would be great if I can get this resolve ASAP.