which Modbus Driver ? - Sungrow Logger 1000A

i have a Sungrow (Brand) - model 1000A Logger for a solar energy system.

i can easily communicate (using Modbus CAS Scanner - freeware tool) to the unit and it returns valid data in correct format as i expect.

however, when i use plant SCADA 2023R2 comms with same settings i cannot connect to it?

does anyone have any experience with comms to these loggers? currently i am using MODNET (which has been successful with about 20 other Modbus TCP devices i have) i was going to try the others, but it looks like there is a vast amount of differing Modbus drivers.

Parents Reply
  • Hi Vishal,

    yes i needed to add the parameter to the ini file "Specifically" for that device ONLY (i have other devices on Modbus TCP). the driver i used was MODNET for my comms. the issue with my device was the SCADA driver would not initialize the device i think , hence the parameter that must force a read of address 030001.

    a free tool that i found handy for fault finding was "CAS Modbus Scanner" which could easily read the device. SCADA support also used "Wireshark" software to diagnose the SCADA driver issue.