We are using Plant Scada 2023 R2 and OFS 3.63 SP3. When we are communicate to Quantum over modnet alarm server works but when we are trying to communite over OFS in this time alarm server doesnt work. any alarm doesnt come to scada.
We are using Plant Scada 2023 R2 and OFS 3.63 SP3. When we are communicate to Quantum over modnet alarm server works but when we are trying to communite over OFS in this time alarm server doesnt work. any alarm doesnt come to scada.
Hi NAmık Kemal Yıldız ,
I assume that you are using OFSOPC driver in your Plant SCADA project in communication with OFSOPC server. Are your server components running in the service mode? Please refer to the following KB article on Aveva Technical Support website. Hope it will help you to resolve the issue.
https://softwaresupportsp.aveva.com/en-US/knowledge/details/000035307?lang=en_US
Regards,
Jacky
Thanks Jacky. We tried it but in this case OFS stoped working. Do you have any other suggestion ?
Hi NAmık Kemal Yıldız ,
Please take a look at section of "Chapter 5. OFS as NT Service" of OFS user manual that should be installed along with OFSOP server. Have you tried OFS client to verify OFSOPC server works properly before running Plant SCADA project? You should also review the OFS configuration with OFS Configuration Tool.
Hi NAmık Kemal Yıldız ,
Please take a look at section of "Chapter 5. OFS as NT Service" of OFS user manual that should be installed along with OFSOP server. Have you tried OFS client to verify OFSOPC server works properly before running Plant SCADA project? You should also review the OFS configuration with OFS Configuration Tool.